    We have just upgraded our KRC2 to version 5.2.12 HF5. Everything is working, apart from the DeviceNet. It is giving an error "6503 Configuration Error I/O DN2DRV"
    Our IOSYS.INI file includes :-
    [DRIVERS]
    DEVNET=2,dnInit,dn2drv.o
    [DEVNET]
    ;------- Inputs ---------
    INB0=10,0,x2
    ;------- Outputs --------
    OUTB0=10,0,x2
    and DEVNET.INI is
    [krc]
    debug=0
    baudrate=500
    [1]
    macid=10
    The MACID of the DeviceNet module (Beckhoff BK5200) is definitely set to 10 on the DIP switches, and the baud rate is set to 500.
    The only difference between this KRC2 and our other KRC2 is that the DeviceNet connector is in a different place on the PC. It appears that this one is on an ISA card - would that cause the problem?
    Any ideas ? :hilfe:
  • Hallo Martin,
    please activate an other driver in IOSYS.INI as follow and deactivate DEVNET:
    [DRIVERS]
    MFC=0,mfcEntry,mfcdrv.o
    ;DEVNET=2,dnInit,dn2drv.o
    [MFC]
    INW0=10,0,x1 ;$IN[1-16]
    OUTW0=10,0,x1 ;$OUT[1-16]
    Try it and give feedback.
    Regards
    Cäsar
  • Hallo, was macht Ihr da ? :waffen100:
    Wenn Du das DeviceNet benutzt sind Deine Einstellungen in der IOSYS.INI richtig.
    Ich frage mich aber, wo Ihr das Kabel reingesteckt habt :huh:
    Es gibt nur einen grünen DeviceNetstecker in der KRC2, auf der MFC !
    Mir scheint, Ihr habt eine LPDN-Scannerkarte eingebaut. Dann müsst Ihr aber
    die Treiber DNSCx=12,dnscxInit,dnscxdrv.o aktivieren
    @Cäsar: der MFC-Treiber ist bei einer KRC2 für das CAN-IO-Modul (16E/20A) gedacht und braucht keine MAC-ID-Angabe (default 1).
  • Problem is, I bought a robot from someone who didnt give me all the information :wallbash:
    The MFC card is in the PC and has DeviceNet connector X801 and RJ-45 X804. X801 was pre-wired to a board A30 X943.1 where there are three DeviceNet connectors, .1 .2 and .3
    I have wired X943.2 to my Beckhoff BK5200 using a Beckhoff ZS1052-3000 connector (which has a switchable Termination Resistor, set to ON.)
    The top LED on the Beckhoff unit shows RUN always (means Status is OK). The Connect LED flashes first (means Ready and waiting for Communication) and then stays always on (means Assigned and OK). I have a new spare BK5200 unit, and I tried this but it made no difference.
    Someone else told me to run dnShow in Telnet, and this is what it gave :-
    DN2DRV Version 1.22.5.0
    Scanner Enable running
    Scanner State OK
    CAN Errors 0
    CAN Overflow 0
    SystemTime -86674677
    BaudRate 500 KBaud
    [00]KRC State 00 Master none
    I:
    O:
    [10] Warn 0 State 30:30 running online
    I: 00 00 00
    O: 00 00
    Value = 1 = 0x1
    Does that help at all ? :kopfkratz:
    Einmal editiert, zuletzt von MartinH ()
  • Hi Martin,
    sorry about my last message in german. I didn't recognize you wrote in english :oops:
    I guess the 24V are missing on the Devnet-Bus:
    - are 24V connected to the MultiPowerTap (A30) ?
    I couldn't find the connector ZS1052-300 on the Beckhoff page :(
  • ok Martin,
    please, change the iosys.ini to 3 input bytes (don't forget IO-Reconfiguration)
    [DEVNET]
    INB0=10,0,x3
    OUTB0=10,0,x2
    if you use the parameter 1 with command dnShow (dnShow 1) you'll get more informations :P
  • :oops: :oops: :oops:
    When installing 5.2.12, it is always a good idea to select MFC2 driver instead of MFC1 driver. This REALLY helps when trying to work with DeviceNet :oops:
    The way I found the problem in the end was to look at number of Network Connections available in Win XPe. Even though I have RJ-45 option on the MFC card, it did not have a Network Connection for me to use (other than VxWorks) so I was not able to connect to our network. This set me thinking about which driver I had chosen when installing . . .
    I have just done a complete reinstall of XPe and 5.2.12, selected MFC2 ( :oops:) driver and it worked first time :supi:
    Very very :oops:
    Many thanks for your help LindePaul :danke: