Kuka KRC2 Profibus Configuration. (Create .ldb file)

  • Install Simatic NCM PC 5.3


    Setup files in the KRC2 D:\Internat\Bus\Profibus\NCM_PC


    Follow Steps.


    1) Run The Simatic NCM PC Manager.
    2) File>New>Project Name>Enter
    3) Project name right click> Insert New Object > Simatic PC Station >Enter
    4) Simatic PC Station> Configuration>Open Configuration Screen
    5) In the Rack, click Rail 1
    6) Right Frame Simatic PC Station Click +
    7) CP Profibus> CP 5614 A2 (For KRC1, CP5613) under SW 6.2. You see Network Configuration Screens. Make adress 1 and Click New. Jump the Network settings and prove settings. Transmission Rate 1,5 Mbps, Profile DP Higgest Bus Address 126. Ok.
    Click again right frame Simatic PC Station under User Application. Open +> Application SW 6.3 select.
    9) 1. Rail interior on the CP 5614 A2 Right click> Add Master System
    10 ) Select The Dp Master Application> Application> Ok
    11) Add Profibus Module.
    12) Setting modul adress. 1. Rail interior CP5614 A2 right click again > Object Properties> Operating Mode > Create LDB file checking> Browse> Select .ldb file saved path.
    13) Save and Compile
    14) Your .ldb files Copy to C:\KRC\Roboter\init
    15) Copy to your module .gsd files C:\KRC\Roboter\init
    16) Open the C:\KRC\Roboter\init\pfbmsl.ini
    Find
    MASTER_USED=1
    DATABASE_PATH=init\yourproject.ldb
    Save and close.


    Kuka_HMI Screen> Configure> I/O driver> I/O Driver Reset> Config>Reconfig


    Check communication status,


    Open the C:\KRC\Roboter\init\iosys.ini file.


    Find [PBMASL]


    INW(Word begin)=Modul adress,0, X(I/O Word Lenght)
    Sample:
    INW12=4,0,X6


    Description:
    The 4. Module I/O adress KRC2 $IN[72].....$IN[168]
    INW12= 12*16(1 Word 16 Bit)= 72th Input (Beginning adress)
    x6= 6*16=6 Words=96 bit=72 Beginning adress+96 bit Data lenght= In 72 to In 168


    Save iosys.ini
    Kuka_HMI screens> Configure> I/O driver> I/O Driver Reset> Config>Reconfig


    If not work the bus system, check the module adress and .gsd files.

    Einmal editiert, zuletzt von Murat ()

  • Schritt für Schritt zum Roboterprofi!
  • Moin,
    der NCM Manager befindet sich nicht auf der Robotersteuerung. Das Progrämmchen ist vom Onkel SIEMENS.
    Alternativ kann man die ldb-Files mit COM-Profibus oder mit dem SIMATIC Manager erzeugen. Ebenda beides von SIEMENS .
    Grüße

    never touch a running system

  • on the siemens DVD inside the blue and white box inside your Robotcontroller

    Wolfram (Cat) Henkel

    never forget Asimov's Laws at the programming of robots...

    "Safety is an integral part of function. No safety, no production. I don't buy a car without brakes."


    Messages und Mails mit Anfragen wie "Wie geht das..." werden nicht beantwortet.

    Diese Fragen und die Antworten interessieren jeden hier im Forum.


    Messages and Mails with questions like "how to do..." will not be answered.

    These questions and the answers are interesting for everyone here in the forum.

Erstelle ein Benutzerkonto oder melde dich an um zu kommentieren

Du musst ein Benutzerkonto haben um einen Kommentar hinterlassen zu können

Benutzerkonto erstellen
Neues Benutzerkonto für unsere Community erstellen. Geht einfach!
Neues Benutzerkonto erstellen
Anmelden
Du hast bereits ein Benutzerkonto? Melde dich hier an.
Jetzt anmelden